Post by dwstucke on Jul 22, 2011 8:06:17 GMT -5
I'm looking for experience regarding what wire gauge to use between a Power Converter and 12v Battery.
My run is about 6 feet and I have some 12 AWG wire but I am concerned that it might not be thick enough. The converter is a 45amp Power Wizard. I don't plan to draw a of of power (lights and a fan) but I'm wondering about the load during the charging cycle.
-Don
|
|
|
Post by avannoy on Jul 22, 2011 11:54:19 GMT -5
|
|
vikx
3K Post Member
Posts: 3,556
|
Post by vikx on Jul 23, 2011 1:16:45 GMT -5
I agree, 10 ga. minimum, I use 8.
|
|
dwstucke
50 Post Member
1963 Shasta Airflyte
Posts: 73
|
Post by dwstucke on Jul 23, 2011 21:30:19 GMT -5
I've ended up using 6 AWG wire. Turned out to be cheaper than 8 because I found it locally by the foot, I could only find the 8 AWG in 100' spools.
Thanks for the help. I was important to learn that 12 AWG wire really was not up tot he task.
-Don
|
|
mikec
New Member
Posts: 10
|
Post by mikec on Feb 1, 2012 22:16:26 GMT -5
One thing you can do if you already have 12ga wire is to double it up, then connect it back together at the ends. 2, 12ga stranded wires are equal to 1, 8 ga single wire and usually alot cheaper too. A trick I learned in outdoor lighting where 8 ga is very expensive.
|
|